The Four Seasons Radon test started Saturday at 12:00 pm. A CO2 test is running concurrently to track the Air Change per Hour (ACH) to determine how ventilation affects the build up of Radon. The background Radon present in the empty room (50 hour test a couple days before) was .775 pCi/L of Radon.
We made a couple of changes in the testing, neither of which will affect the outcome, just made it easier to do the test. First we added a window to the room, caulked and screwed in place, then sealed with plastic box tape. And yeah, I forgot to clean the window...
The ACH of the room could possibly change from the previous value of .03 ACH, which is about 23 cubic feet of air change per hour. This is pretty tight for a room, but condos have been reported at near these levels so this is not an unobtainable ACH. But with the CO2 test running concurrently with the Radon test, this test will have the ACH established every five minutes. So the Radon is being measured, the CO2 levels, also the relative humidity and temprature.
The second change was our method of raising the CO2 levels in the room for the ACH test. We had been using dry ice, but an eight pound block costs about $9.00 and lasts only about a day and a half in the freezer, so only one test can be done. But more importantly, it was difficult to keep from putting too much CO2 into the room, which meant that the CO2 had to decay for about 24hours before the data logger started showing the drop in CO2 due to room leakage. The meter itself is capable of measuring higher ppm levels than the Hobo data logger was capable of recording.
So we tried the small CO2 cartridges used for BB guns. Go to the far corner of the room, quickly use a hammer and sharp punch to puncture the end of the cartridges, and get the hatch closed and sealed ASAP. Using three cartridges ($1.50 worth), quickly brought the Radon room up to over 1300 ppm. High enough for the ACH test to give good data, low enough that the data logger could obtain data the same day.
Here is the first 24 hours of data, in graph form. Double click on the small graph picture to see a larger, readable version. As you can see, the Radon is climbing steadily, up to 4.9 pcI/l. After subtracting the .775 pCi/L background Radon, there is 4.145 pCi/L of new Radon in the room.
Is the room tight? It is, but this is only one day's result and it should keep climbing for many days. Increased ventilation will slow the rise of the Radon, and if enough ventilation is present, it will prevent the rise past some point. One of the experts is going to look over the data this weekend, do some calculations, and might have some ideas on what might happen as the test progresses.